Democratic Underground Latest Greatest Lobby Journals Search Options Help Login
Google

An electrical tip so you don't go nuts like I did

Printer-friendly format Printer-friendly format
Printer-friendly format Email this thread to a friend
Printer-friendly format Bookmark this thread
Home » Discuss » DU Groups » Home & Family » DIY & Home Improvement Group Donate to DU
 
Jersey Devil Donating Member (1000+ posts) Send PM | Profile | Ignore Tue Nov-14-06 11:15 PM
Original message
An electrical tip so you don't go nuts like I did
Edited on Tue Nov-14-06 11:18 PM by Jersey Devil
OK, so I was replacing a light/fan/heat combo unit in the ceiling of my master bathroom that was almost 25 years old. I took down the old unit and discovered the wires to the heater were absolutely fried, the insulation cooked right off of them because it was a 20 Amp rated unit on a 15 Amp line, installed by an electrician no less, when the home was built 25 years ago. The damned house could have burned down due to his negligence.

So I found a good replacement online by Broan that was a unit rated for a 15 Amp line, and assured that this time, despite it being a doityourself job, there would be no chance of burning the house down.

I installed the new one without much of a problem until I tried to test it and ran up and down the goddamned stairs to the circuit breaker maybe 30 times before I realized that I probably had an additional problem - the switch was bad too!

So, tip #1 to myself - Always double check the amount of amperage for any electrical appliance/fixture against the rating for the electrical supply line for it.

Tip #2 - To prevent excess wear and tear on your legs and feet, change the goddamned switch you are working on for the outlet you are replacing at the same time.

That is all, goddammit!

Refresh | 0 Recommendations Printer Friendly | Permalink | Reply | Top
eleny Donating Member (1000+ posts) Send PM | Profile | Ignore Fri Nov-17-06 05:05 PM
Response to Original message
1. Good advice
We had some electrical work done a few years ago. One of the ceiling lights was evidently too much for the wires. They were practically all melted into one glop. A real modern art sculpture living up there in the ceiling preparing to set the attic and roof on fire.

All the lines have been checked and replaced as needed. Now the house is safe for all our needs.
Printer Friendly | Permalink | Reply | Top
 
lumberjack_jeff Donating Member (1000+ posts) Send PM | Profile | Ignore Thu Nov-23-06 09:58 AM
Response to Original message
2. In older houses...
it is not uncommon for previous owners to replace 15a breakers with 20a. If the wiring is 14ga, this can be dangerous. A 20a circuit requires 12ga wire.

I'm surprised that the breaker didn't trip prior to wire/switch meltdown.

I'm also surprised that they make 110v ceiling fan/heat combos that require a full 20a. By way of comparison, a normal heat lamp bulb takes only 2.1a. 20a=2400w.

Aluminum wire was used in the 60's. It's dangerous. If you find it, call an electrician.
Printer Friendly | Permalink | Reply | Top
 
Jersey Devil Donating Member (1000+ posts) Send PM | Profile | Ignore Fri Nov-24-06 12:27 AM
Response to Reply #2
3. Yes, thanks
Edited on Fri Nov-24-06 12:29 AM by Jersey Devil
Most of the wire in my home (except the kitchen and AC) is 14ga/15a. The unit I removed did not have a heat lamp but a metal coil like a toaster over which a fan blew air. I replaced it with a Broan unit (also with a coil) that specifically states a 15a line is enough. If you look at the Broan and Nutone web sites you will see that virtually all of their heater units required a 20a line.

Why didn't the breaker trip? I suspect it was because the heater was still working and though the insulation was fried off the hot wire feeding the heater inside the unit's box it was still making contact and there was no short.

I've seen this type of thing before on outlets in the house that were backwired when installed (wire inserted in a hole in the back of the switch/outlet instead of screwed in). In a few of them the outlet was actually partially melted at the connection because it worked loose (I guess due to vibration) but still were connected close enough so that they would arc to make a connection, creating a lot of heat. Backwiring is not permitted in NJ anymore.
Printer Friendly | Permalink | Reply | Top
 
Another Bill C. Donating Member (1000+ posts) Send PM | Profile | Ignore Fri Nov-24-06 10:25 AM
Response to Reply #3
4. Backstab vs. backwire
The kind of outlet or switch where you insert a wire in the back to be captured by spring tension is called a "backstab" switch or outlet. These are bad.

The kind of outlet or switch where you insert a wire in the back but clamp it in place by way of a screw is called a "backwire" switch or outlet. These are good.
Printer Friendly | Permalink | Reply | Top
 
Jersey Devil Donating Member (1000+ posts) Send PM | Profile | Ignore Fri Nov-24-06 12:10 PM
Response to Reply #4
5. Thanks - I meant backstab
I was using the wrong terminology. Mine were 'backstab' and I have been changed them out room by room as I repainted the house.
Printer Friendly | Permalink | Reply | Top
 
DU AdBot (1000+ posts) Click to send private message to this author Click to view 
this author's profile Click to add 
this author to your buddy list Click to add 
this author to your Ignore list Wed Apr 24th 2024, 05:07 PM
Response to Original message
Advertisements [?]
 Top

Home » Discuss » DU Groups » Home & Family » DIY & Home Improvement Group Donate to DU

Powered by DCForum+ Version 1.1 Copyright 1997-2002 DCScripts.com
Software has been extensively modified by the DU administrators


Important Notices: By participating on this discussion board, visitors agree to abide by the rules outlined on our Rules page. Messages posted on the Democratic Underground Discussion Forums are the opinions of the individuals who post them, and do not necessarily represent the opinions of Democratic Underground, LLC.

Home  |  Discussion Forums  |  Journals |  Store  |  Donate

About DU  |  Contact Us  |  Privacy Policy

Got a message for Democratic Underground? Click here to send us a message.

© 2001 - 2011 Democratic Underground, LLC